    Hi: When wiring a detached garage or shop with 60 amps #6 teck, Fed from a 60 amp breaker in my house, do i need to:
    1) Have a ground rod at the garage/shop
    2) Have a disconnect at the Garage/shop
    3) Have a Main breaker or just a loadcenter at the garage. CEC Rules? Thanks

  2. #2
    Inactive Member neil seidner's Avatar
    Join Date
    October 19th, 2003
    Posts
    127
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    I can't give you the exact code rules because I don't have my code book with me at this time but:

    1. You don't need a ground rod, you only need a ground rod if the feed does not have a ground wire (teck cable has a ground wire), or if the detached building is used to house livestock.

    2. You don't need a disconnect in the shop, the disconnect has to be in the house panel, and the 60A breaker does this job.

    3 The shop panel does not have to be a combination panel, but I here a combination panel might be cheaper than a panel without a main breaker.

    P.S. If you are not using a grounding rod, make sure the neutral-to-ground jumper is removed from the shop panel. The electrical inspector will always look at this.

  3. #3
    Inactive Member lesmcw's Avatar
    Join Date
    February 14th, 2004
    Posts
    5
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks CCrash (Neil)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •